#11
|
||||
|
||||
![]()
Tässä hydronic 10:n ohje:
Delete fault memory Condition: An electrical connection exists from terminal 15 (ignition) to the module timer, 12-pin connector, chamber 10. • Correct cause of fault. • Press button c –> The heater is switched on. (liekin kuva) • Press button a,(kello) keep it depressed and then press button p within 2 seconds. The module timer is now in the „Enquire fault memory“ program. • Switch off ignition (terminal 15). • Simultaneously press button a (kello) and button p, in addition, switch on the ignition (terminal 15) and wait until the following appears in the display. After ignition „ON“ the following appears in the display: Display flashes, heater symbol does not flash • Switch the heater off and on –> the control box is unlocked, the heater restarts. |